可否再帮忙翻译下以下这段话,万分感谢。

昨天我们在吊运主机排气阀时突然机舱行车不能进行升降控制,检查行车控制箱发现控制箱内电源开关3F1
发生跳电,我们对其进行复位,但还是马上跳电。我们收到并阅读了厂方相关图纸和说明书后,于今天对行车故障继续进行检查,将接线(X1. 18, X1.19)从接线排脱开,对3F1进行复位,发现开关能合上,说明从控制箱到吊机升降马达刹车整流电路的电源线没有问题,问题出现在给刹车线圈提供电源的整流电路上,整流电路二极管损坏造成交流侧短路进而造成电源开关3F1跳电。我们也测量了HOISTING MOTORS(3M1.1, 3M1.2)的绝缘电阻及三相绕组线圈,发现正常;卸下HOIST BRAKE 线圈(前面的3Y1没有找到,而图纸上是有的)的接线并测量绝缘和绕组线圈,也发现正常。现我们对给HOIST BRAKE提供电源的整流电路集成电路板(A1)进行索赔,并要求厂方尽快将其供船(由于该电路的损坏,在吊装排气阀时我们只能用葫芦费了九牛二虎之力才将排气阀装入,但拆下的排气阀由于放在主机缸头层没法吊走,对安全很不利,且主机另外两个排气阀也急需更换,但现在这些工作都无法完成。)。

第1个回答  2011-03-08
尝试联系你无果,实际上就是要说你这个是高度专业化的翻译,强烈建议寻找电气或机械工程专业的人士进行磋商而不是仅找会英文的人。以下的翻译仅供最粗浅的参考。部分我不确定如何翻译得专业词汇我用引号标记了出来,并在后面的括号中注明其本应对应的中文。其实最关键的是那个“给HOIST BRAKE提供电源的整流电路集成电路板”,就是那个你让厂方索赔的东西的翻译要十分十分的准确,毕竟是索赔对象嘛!!

Yesterday when we were carrying the “drain tap” (排气阀) of the “mainframe” (主机) we found that the hoister for the “engine room” (机舱) couldn’t perform hoisting. After checking the control box of the vehicle we found the switch 3F1 tripped, even after we tried to reset it. After we had received and read the drawings and handbooks from the factory, we checked the vehicle again, pulling the wire (X1.18, X1.19) off from the plug board and resetting switch 3F1, only to find that the switch worked well. This proved that there was no problem in the “rectified circuit” (整合电流) between the control box and the “hoist brake motor”(升降马达刹车),and that the problem occurred in the rectified circuit of the power supply for the hoist brake’s coil. More specifically, the malfunction of the“diode rectifier” (整流二极管) short-circuited the AC side of the whole circuit, furthermore causing switch 3F1 to trip. We also checked the insulated resistor and “三相绕组线圈” (实在不知道怎么翻译) and they worked as normal. Thus now we claim the cost of A1“IC board in the rectified circuit” (整流电流集成电路) that supply power for the hoist brake and request that the factory “将其供船” (不知何意) (Due to the damage of that circuit, we went through painstaking procedures to hoist and install the drain tap. Yet we are not able to move away the removed drain tap, (这里没有翻译“只能用葫芦”,因为不知道是什么意思) which is now placed on the top floor of the “mainframe vat” (主机缸), which is very unsafe. We are also unable to remove other two drain taps in urgent need of removal.)

P.S. 我一般不这样说其他人,但你这段话涉及严肃重要的话题,我不得不说,仅从文法正确和通畅角度前面1至4楼的翻译都没有我的准确。而专业术语的翻译我们几个半斤八两,如前述请你务必找专业人士咨询,不是开玩笑的。追问

非常感谢您的翻译。呵呵,在您翻译之前我已译好了,基本上差不多,只是语句方面作了调整,有些专业用词改了过来。

第2个回答  2011-03-08
Yesterday we lifted the host when the exhaust valve lift suddenly can not control the vehicle cabin, check the traffic control box found in the control box power switch 3F1
Tripped power, we reset them, but still jump at power. We have received and read the factory-related drawings and specifications, the failure to continue today to check on the vehicle, the wiring (X1. 18, X1.19) disconnected from the terminal block on the 3F1 reset, that switch can be closed , that from the control box to lift the crane motor brake rectifier power cord is no problem, the problem in the brake coil to provide power to the rectifier circuit, the diode rectifier circuit damage caused by short circuit and cause the AC side power switch 3F1 jumping power. We also measured the HOISTING MOTORS (3M1.1, 3M1.2) insulation resistance and three-phase windings, that is normal; remove HOIST BRAKE coil (in front of the 3Y1 is not found, but the drawings are some) of the wiring and measure insulation and windings, also found normal. HOIST BRAKE now we provide power to the rectifier circuit integrated circuit board (A1) to claim, and called for the factory as soon as the ship (due to damage to the circuit, when the exhaust valve in the lifting hoist we only took nine before the power of cow tigers into the exhaust valve, but removed the exhaust valve on the master cylinder as the first layer hanging can not go very bad for security, and the exhaust valve is also host two other much-needed change, but Now these are not complete.).本回答被提问者采纳
第3个回答  2011-03-08
Yesterday we were hoisting host vent suddenly cabin driving cannot undertake lift control, check traffic control box found control box power switch 3F1
Happen jump electricity, we carry on the reduction, but still leapt electricity. We received and read manufacturer related drawings and specifications, from today on the traffic fault continue to inspect, wiring (clamps its X1. 18, X1.19) from wiring row withdraw, to 3F1 are reset, and found that the switch can close, explain from lifting motor control box to crane brake rectifier circuit power without question, the problem of coil to provide power to brake rectifier diode rectifier circuit circuit, damage caused by exchange short-circuit causing the power switch 3F1 jump electricity. We also measured

HOISTING MOTORS (3M1. 1, 3M1... 2) insulation resistance and three-phase windings, found normal, Unload HOIST Volkswagen coil (front 3Y1 not found, while drawing is some) of wiring and measuring insulation and the windings, also found normal. Now our to provide power to HOIST Volkswagen of rectifier circuit chips (A1) for the compensation, and requires the manufacturer as soon as possible for ship (due to the damage of this circuit, in hoisting vent valve when we can only use gourd had the dickens will vent load, but due to remove the exhaust valve on host of cylinder head layer can't walk, the safety hang is bad, and host the other two vent also need change, but now these tasks are unable to complete. .
可以了
第4个回答  2011-03-08
Yesterday we while hanging luck host row to annoy valve suddenly the passenger compartment went a car to carry on to ascend and descend a control, the check goes a car control the box discovered the control power switch inside the box 3 F1s
The occurrence jumps an electricity, as to it's do we carry on resetting, but still keep jumping an electricity right away.We receive and after reading the factory square related diagram paper and manual, continue to carry on a check towards going car breakdown today, will connect line(X1.18, X1.19)from connect the line row takes off to open and carries on resetting to the 3 F1s, discover the switch can close and explain from the control box to hang the power cable that the machine rise and fall motor brake commutates electric circuit to have no problem, the problem appears in providing commutating of the power electric circuit for brake coil and commutate electric circuit diode the damage make the side short circuit then resulted in the power switch 3 F1s' jumping an electricity.We also measured HOISTING insulating of MOTORS(3 M1.1s, 3 M1.2s) electric resistance and three mutually round a set of coil, discover as usual;Unload connecting of the coil of HOIST BRAKE(front of the 3 Y1s didn't find out, and diagram paper ascend certain) line and measure to insulate and round a set of coil, also discover as usual.Now we to give HOIST BRAKE to provide the power of commutate electric circuit integrated circuit the plank(A1) carry on claim, and request a square of factory to provide the ship he/she as soon as possible(because of the damage of that electric circuit, while hanging to pack row spirit valve we can be used a bottle gourd fee the dint of the tremendous amount just will line up spirit valve to pack go into, but dismantle next of row spirit valve because of put can not mourn to walk at the host urn head layer, very disadvantageous to safety, and host moreover two row spirit the valve also need replace urgently to, but these works can not complete now.).
第5个回答  2011-03-08
Yesterday we were hoisting host vent suddenly cabin driving cannot undertake lift control, check traffic control box found control box power switch 3F1 happen jump electricity, we carry on the reduction, but still leapt electricity. We received and read manufacturer related drawings and specifications, from today on the traffic fault continue to inspect, wiring (clamps its X1. 18, X1.19) from wiring row withdraw, to 3F1 are reset, and found that the switch can close, explain from control box to crane

Lifting motor braking power rectifier circuit: no problem, the problem of coil to provide power to brake rectifier diode rectifier circuit circuit, damage caused by exchange short-circuit causing the power switch 3F1 jump electricity. We also measured HOISTING MOTORS (3M1. 1, 3M1... 2) insulation resistance and three-phase windings, found normal, Unload HOIST Volkswagen coil (front 3Y1 not found, while drawing is some) of wiring and measuring insulation and the windings, also found normal. Now our to provide power to HOIST Volkswagen of rectifier circuit chips (A1) for the compensation, and requires the manufacturer as soon as possible for ship (due to the damage of this circuit, in hoisting vent valve when we can only use gourd had the dickens will vent load, but due to remove the exhaust valve on host of cylinder head layer can't walk, the safety hang is bad, and host the other two vent also need change, but now these tasks are unable to complete.